No, generators are either closed delta or wye.
480 is nice, until you buy a 600 volt disconnect.
IMO the cadillac of three phase is a closed delta. Perfect phase angles and higher voltage will make sirens scream. Usually a 240 delta setup will run between 240-255 volts phase to phase, and 480 delta will be around 490-500 volts.
480 wye is fine, but 208 wye sucks. Everything runs slower and hotter.
The corner grounded delta (
widowmaker) is being phased out (no pun intended) but they are still quite prevalent on remote three phase installations. They have only two insulated wires in the service drop, with the bare messenger carrying the third phase which is bonded to ground at the transformer tank. Since that particular phase is referenced to ground, it will read 0 volts phase to ground, but show either 240 or 480 phase to phase. Just because it's a "grounded" phase doesn't mean it's not dangerous. If you grab it you will get lit up since you are at a different ground potential than the transformer tank. It's also known as the ghost leg or phantom leg.
There is also an open wye-wye connection, but it's not very common. Most 2 pot banks are connected wye-delta or delta-delta.
Also it is possible to have three phase power with just one transformer. They aren't very common but they are out there. You can spot them easy since they usually have three insulators on top of the tank.
If you know how to "read" the secondary side connections on the transformers it's easy to differentiate between a closed delta or wye setup. Wye banks have all the neutrals tied together, whereas a delta bank will only have 1 neutral coming off 1 transformer. If it doesn't have any neutral taps it's a 3 wire delta setup (usually 480). If it has a bare wire coming off a power leg on the transformer with a bonding jumper attached to that bushing it's a corner ground.
Another tidbit, if you look at an open delta often times they will have a big transformer and little transformer. The big transformer supplies two phases and is often center tapped for single phase loads, so it's bigger. The little transformer (kicker or lighting pot) only has to supply one phase and it's always the high leg. This how you can feed several houses and a three phase load with a two pot bank. The big pot delivers the single phase load to the houses, while the little pot and the big pot supply three phases to a three phase load. The houses will never see the high leg since they aren't connected to the "kicker".
One last thing, NEC requires that the high leg always be on B phase and flagged orange for 240 or purple for 480. However, most electrical meters will not read properly if they have the wild leg on B phase. So a standard practice is to place the wild leg on C phase, then move it to B phase on the disconnect or panel board.
Here is a three phase, 4 wire delta meter base before I wired it up. The orange wire would go on C phase, with the black wire on A phase, and the blue wire on B phase. The white wire is the neutral.
Here is an open delta bank feeding a Thunderbolt in Holliday, TX
Notice how they only have two overhead phases on the primary side? That's the beauty of an open delta. You can get three phases out of the secondary side by connecting two transformers to two primary phases and referencing the neutral.