Re: Is this 3 phase?
Posted: Wed Mar 12, 2014 11:52 am
Well, it depends on the transformer. They make single transformers that are actually three transformers in one can. The majority of three phase power is derived from connecting 2 or 3 single phase transformers in Wye or Delta.I'd rather bump this topic than start a new one, but I'm still confused on a few phase things.
1. This one is more of a clarification, but a 3 phase siren can run off 1, 2, or 3 transformers, given that they are able to produce power, right? And are pretty much all single phase siren setups run off of 1 transformer?
Well, it depends on the service. You have three phase 3 wire (no ground), 3 phase 4 wire (3 hots & a neutral), and three phase corner ground, which has two insulated wires and the third phase is carried in the bare messenger. Keep in mind that the neutral is usually brought in through the messenger wire, so for a 3 phase 4 wire service you will have three insulated wires in the service drop and the neutral connection will be made on the bare messenger.2. In terms of wires going into the siren, how many are needed to provide power for a 3 phase siren and a single phase siren?
Single phase comes in 120 only (one wire and messenger), 240 only (no neutral), and 240/120 (2 wires and a neutral messenger)
All DC sirens are single phase. They can run off a three phase service since two legs of three phase 208/230 is single phase. Most of the time they just tie back the unused leg when they replace a three phase siren with a DC. All P-50s are three phase, no exceptions.3. Since my area is filled with Tempests, are T-128 and T-135s offered in both single and 3 phase varieties or they all 3 phase? Same question with 2001s as well. The ones around are seen with both one transformer and 2 transformers. Also, I believe all P-50s are 3 phase as well, am I right?
You can have 480 three phase from two transformers via an open delta transformer bank connected for 480. Delta banks tend to run at a higher voltage than wye banks (I've seen 490 volts on a 480 delta before). That explains the rapid windup. Delta is awesome, it makes sirens run like a bat out of hell.4. I thought that in order to have 480V, you would need 3 transformers, however, I'm seeing this P-50 run off of 2 transformers, yet have a very fast windup. What am I missing here?