Is your phase converter rated to start the horsepower load of the motors it will be running? It seems like your phase converter may be large enough to 'run' the motors in question , but not to 'start' them. If the static converter freaks out when the motors present their starting load, it may make sense to use a rotary phase converter instead, since it would be too "dumb" to try and crank up the voltage extra-high. Then, just oversize the rotary phase converter by 1.25 or 1.5 for safety factor.
Here in West Lafayette, IN, there are some smaller sewage lift stations way out in the sticks that use rotary phase converters. They just use TEFC idlers and mount them to a concrete pad beside the control cabinet.