Im an electronics guy. This makes me happyOhio_Man wrote: ↑Fri May 22, 2020 1:53 am"No Tim I don't think that's right" -Al Borlean, Home Improvement.kb8vul wrote: ↑Thu May 21, 2020 10:09 pmuncommonsense wrote: ↑Thu May 21, 2020 9:52 pmAbsolutely not. Its possible if you want to burn your house down from an electrical fire. The draw would be far too much for 120V to handle.
You SURE about that?
An STH/L-10 is fused at 50 amp at 240 volts.
So the the current draw from the same load and half the voltage would be half the current.
So 25 amps. Mind you a 15 amp breaker which is typical for a run of the mill outlet would pop almost immediately.
But a 20 amp or 30 amp breaker, fed with the correct wire, would probably hold and run the motor up to not quite half speed.
That being said, if you would need to run a new circuit, why not install a CORRECT circuit with a proper 50 amp outlet and a manual disconnect (could use a 50 amp welding outlet)
and just be done with it.
But as far as burning down the house,,,, only if the wiring in the house was improper, the fuse / circuit breaker was improper would you chance a house fire over the attempt.
If everything was right and you were to try it, the 15 amp breaker would just pop and that would be the end of it.
Volts X amps=watts.
The siren draws 50 amps at 240V. A motors wattage cannot be changed. If you run that motor at 120V, It will pull 100 amps.
Uhhh, NO. And I think I covered WHY.Timmy-73 wrote: ↑Mon Jul 20, 2020 9:14 pmIm an electronics guy. This makes me happyOhio_Man wrote: ↑Fri May 22, 2020 1:53 am"No Tim I don't think that's right" -Al Borlean, Home Improvement.kb8vul wrote: ↑Thu May 21, 2020 10:09 pm
You SURE about that?
An STH/L-10 is fused at 50 amp at 240 volts.
So the the current draw from the same load and half the voltage would be half the current.
So 25 amps. Mind you a 15 amp breaker which is typical for a run of the mill outlet would pop almost immediately.
But a 20 amp or 30 amp breaker, fed with the correct wire, would probably hold and run the motor up to not quite half speed.
That being said, if you would need to run a new circuit, why not install a CORRECT circuit with a proper 50 amp outlet and a manual disconnect (could use a 50 amp welding outlet)
and just be done with it.
But as far as burning down the house,,,, only if the wiring in the house was improper, the fuse / circuit breaker was improper would you chance a house fire over the attempt.
If everything was right and you were to try it, the 15 amp breaker would just pop and that would be the end of it.
Volts X amps=watts.
The siren draws 50 amps at 240V. A motors wattage cannot be changed. If you run that motor at 120V, It will pull 100 amps.
This^^^^^kb8vul wrote: ↑Tue Jul 21, 2020 2:56 amUhhh, NO. And I think I covered WHY.
So here it is again.
The electrical resistance / impedance (look it up) of the siren motor is going to be a fixed amount. Those that are using the idea that a DUAL VOLTAGE motor with series / parallel windings that WILL draw twice the current to product the same HP output are mistaken, A federal 10 HP 240 volt motor does NOT have this sort of arrangement were it can be wired to 110 natively. If that were the case, then YES, it would draw 100 amps. BUT it's not wound in that manner.
So since the windings are a FIXED impedance when you put HALF the voltage to it, it draws HALF the current and produces HALF the horse power of what it will when the correct voltage is applied.
And again, if you are convinced you are right.... then HOW did I start and run a STH10 on a 14 gauge electrical cord fed by a 15 amp breaker? Hell it didn't even spark when I plugged it in.