About this, I did get the siren running with static but it would go to a certain RPM and the breaker would trip. The converter did get passed the chopper stuff though.kb8vul wrote: ↑Thu Feb 24, 2022 5:52 amWere you using a rotary phase converter or a static converter? Static is just a box, the rotary has a motor with it.
You are NOT going to be able to start a siren with a static converter due to the parasitic load on the motor. The chopper is just too heavy. You will need a rotary converter to do this.
Also, what size breaker are we talking about. If you are trying to start this on a 20 amp breaker you are not gonna have any luck. 50 amp is about the minimum you will need feeding it. And DON"T just swap the breaker from a 20 to a 50. The wiring will not be heavy enough and will cause other problems.
Look at the motor plate and figure out what the rated horse power is. Then find a rotary phase converter that is 50% bigger than the motor rating. That's gonna be a minimum for it to work.
I’ve heard that lol. The guy with the generator I was talking about, he knows a few here and there about the wiring and stuff. I’ll get him to help me out with it.
If it didn't hit full RPM it never fully started.NorCal wrote: ↑Thu Feb 24, 2022 10:22 pmAbout this, I did get the siren running with static but it would go to a certain RPM and the breaker would trip. The converter did get passed the chopper stuff though.kb8vul wrote: ↑Thu Feb 24, 2022 5:52 amWere you using a rotary phase converter or a static converter? Static is just a box, the rotary has a motor with it.
You are NOT going to be able to start a siren with a static converter due to the parasitic load on the motor. The chopper is just too heavy. You will need a rotary converter to do this.
Also, what size breaker are we talking about. If you are trying to start this on a 20 amp breaker you are not gonna have any luck. 50 amp is about the minimum you will need feeding it. And DON"T just swap the breaker from a 20 to a 50. The wiring will not be heavy enough and will cause other problems.
Look at the motor plate and figure out what the rated horse power is. Then find a rotary phase converter that is 50% bigger than the motor rating. That's gonna be a minimum for it to work.
Thanks for the reply. Im not sure about the generator but all I know is, it ran his model 5 flawlessly so it may be able to run the Siren. I don’t know much about power but it’s my honest opinion about the generator.kb8vul wrote: ↑Fri Feb 25, 2022 4:32 amIf it didn't hit full RPM it never fully started.NorCal wrote: ↑Thu Feb 24, 2022 10:22 pmAbout this, I did get the siren running with static but it would go to a certain RPM and the breaker would trip. The converter did get passed the chopper stuff though.kb8vul wrote: ↑Thu Feb 24, 2022 5:52 amWere you using a rotary phase converter or a static converter? Static is just a box, the rotary has a motor with it.
You are NOT going to be able to start a siren with a static converter due to the parasitic load on the motor. The chopper is just too heavy. You will need a rotary converter to do this.
Also, what size breaker are we talking about. If you are trying to start this on a 20 amp breaker you are not gonna have any luck. 50 amp is about the minimum you will need feeding it. And DON"T just swap the breaker from a 20 to a 50. The wiring will not be heavy enough and will cause other problems.
Look at the motor plate and figure out what the rated horse power is. Then find a rotary phase converter that is 50% bigger than the motor rating. That's gonna be a minimum for it to work.
I have been building rotary phase converters for about 20 years now. Mostly for running heavy metal working equipment and 3 phase welders.
The 3 phase generator is a good option to try. If it's over 20Kw it should have no issues running that siren.
Just make sure you use the correct wire gauge, fusing and a disconnect to control the siren.