You'll be fine running the motor without a soft start, as long as you have the correct size starter and overloads.Rampage98 wrote: ↑Wed Jan 11, 2023 11:10 pmThanks Non-Zero for the info. That's pretty much how i've drawn out the power circuit and with 120v control. I do have a 200 amp service box in my shop so that is no prob adding a breaker and rated outlet. The timer seems doable too. My biggest question is slamming 220v without a soft starter. The inrush current would seem crazy especially when they run constant 50+ amps in service. It's def a heavy duty motor in these units. Did they not worry about that in the "old days" with these sirens?